t = (X*H^.1.33)/release rate^(.33)
X=4.6*10^-4*Y^2+2.7*10^-15*Y^6
where Y = DeltaT(given)*H^5/3/release rate^2/3
(Hey, you firefighters donna messaroun', you know dat?)
The Heat Release Rate 250 BTU/s.
The inside temperature is 75 degrees F
The detector alarm temperature is 135 degrees F.
The ceiling height in the living room is 10 ft
The heat detector is located on the living room ceiling, approximately 2 ft. from the centerline of the fire.
The Response Time Index (RTI) of the heat detector is 100.
The fire can be assumed to be Steady State.
Okay: I think the release rate conversion: 1 BTU/second equals 1.0542 kilowatt; 250 BTUs = 264kw
Required temp rise = 135 - 75 = 60 degrees
Y = 60*10ft^(5/3)/264kw^(2/3) = 67.7
X=4.6*10^-4*Y^2+2.7*10^-15*Y^6
X= 2.1
t = (X*H^.1.33)/release rate^(.33)
t = ~7 seconds
*whew*
"Math is Hard"; "Let's go shopping!"
If'n y'all believe my calcs, I'd like ta think the first guy to verify and cut/paste would be a lucky feller!